110811-0909 EDT
JerryR:
In the 1000 series data from the MTU is sent by power line carrier to the display unit. In the display unit there is an interface from that data to a USB port. Via USB the data is sent to a destination that can be a computer. You write your own software or purchase a software program called Gateway that is loaded on the computer.
All the data processing functions and data storage are in the computer. The Gateway is a program on your computer rather than in the Gateway box. Being in a normal computer this function loads faster and much more data storage is available. Basically a large circular buffer is used for the 1 second data and it stores in excess of 24 hours of data. Thus, once a day or at other times that you desire the data can be exported to a specified file for long term storage and external processing. Once you have 1 second data in a file you can do anything you want with that data. One thing I do is data reduction, but still retain useful 1 second data. Exporting data does not change what is in the circular buffer. I normally export the buffer about 2330 each night. But if I want something during the day I do an export at whatever time it is. I use a file name like 110810-2336-edt for yesterday, and set the range starting at 08/09/2011 23:00 and leave the end at 08/11/2011 00:00 .
The way to analyze an individual 120 V load is to put one current sensor on the hot wire to that load, and leave the other current sensor in free space. On a 240 V load use both current sensors, one on each hot wire. Phasing of sensors is important or they subtract instead of adding.
You can not encompass both the hot and neutral wires with a current sensor. If you do the result should be near zero.
To evaluate a refrigerator or similar equipment you make a short extension cord with individual wires, use #14 or #12 wire. Or buy a #14 extension cord, 6 ft, and separate out the hot wire. A useful cord for this purpose is made by Husky sku # 623-395, 9 ft, and is in our Home Depot stores. It has a red and black cord cover. This particular cord is the only one in # 14 that I have found with a straight plug. Most short large wire extension cords are labeled Appliance and have a right angle plug.
You install a 3 prong plug on the 120 V leads to the MTU so it can be plugged into the same outlet as the device to be tested. Also connect the display unit to the same outlet. It is important that the black wire of the MTU go to the neutral pin of the plug.
With this setup you are monitoring the one individual load connected to the split extension cord.
Amprobe makes a device that does this for you, and also has an internal 10 turn coil for increasing sensitivity by 10X. The part number is ELS2A. Maximum current rating 15 A. See
http://amprobe.com/cgi-bin/pdc/viewprod.cgi?pid=2356&tid=1&type=elec . The price is $27 from my electrical distributor. Grainger might have it. It is not stocked by my distributor.
With the problems I have had the past few days I can not recommend the 5000 series.
.